ALTIVAR 71 (ATV71HD) Variable Speed Drives for Asynchronous Motors (Installation manual)


Year: 2005
Language: english
Author: Telemecanique
Genre: Installation manual
Publisher: Telemecanique (Schneider)
Format: PDF
Quality: eBook
Number of pages: 53
Description:
55 kW (75 HP) ... 75 kW (100 HP) / 200 - 240V
90 kW (125 HP) ... 500 kW (800 HP) / 380 - 480V
PROGRAMMING
v 1 Please refer to the programming
manual
b 1 Take delivery of the drive
v Check that the catalog number printed on the label is the same
as that on the purchase order
v Remove the Altivar from its packaging and check that it has not
been damaged in transit
b 2 Check the line voltage
v Check that the line voltage is compatible with the
voltage range of the drive (see pages 8 and 9)
b 3 Mount the drive
v Mount the drive in accordance with the instructions
in this document
v Install and connect the DC choke (see page 11)
v Install any internal and external options
b 4 Wire the drive
v Connect the motor, ensuring that its
connections correspond to the voltage
v Connect the line supply, after making sure that
it is turned off
v Connect the control
v Connect the speed reference

INSTALLATION

Preliminary recommendations
Receipt
The packaging contains two items:
- The drive
- A DC choke
1 Handling and storage
To protect the drive prior to installation, handle and store the device in its packaging.
Ensure that the ambient conditions are acceptable.
2 Installing the drive
- Mount the drive on the wall or in the bottom of the enclosure in accordance with the
recommendations described in this document.
ATV71H D55M3X to D75M3X and ATV71H D90N4 to C50N4 drives must be removed
from their packaging and installed using a hoist. They are fitted with handling lugs for
this purpose. The precautions described below must be observed.
3 Installing the DC choke
ATV71H D55M3X to D75M3X and ATV71H D90N4 to C50N4 drives are supplied with
a DC choke that must be installed on the top of the drive and wired in accordance with
the recommendations described in this document. This choke must be used for
connecting drives to the 3-phase line supply.
For ease of transport, the DC choke is supplied ready-assembled.
- In order to install the DC choke, dismantle it as shown on the diagram opposite.
- Install the DC choke on top of the drive and connect it. The instructions for installing
and connecting the choke are given on page 11.
Chokes must be removed from their packaging and installed using a hoist.
The precautions described below must be observed.

Additional

Installation manual Retain for future use Altivar 71
Variable speed drives for asynchronous motors
55 kW (75 HP) ... 75 kW (100 HP) / 200 - 240V
90 kW (125 HP) ... 500 kW (800 HP) / 380 - 480V
Before you begin
Read and understand these instructions before performing any procedure with this
drive.
DANGER
HAZARDOUS VOLTAGE
• Read and understand this manual before installing or operating the Altivar 71 drive.
Installation, adjustment, repair, and maintenance must be performed by qualified
personnel.
• The user is responsible for compliance with all international and national electrical
standards in force concerning protective grounding of all equipment.
• Many parts in this variable speed drive, including printed wiring boards, operate at line
voltage. DO NOT TOUCH.
Use only electrically insulated tools.
• DO NOT touch unshielded components or terminal strip screw connections with
voltage present.
• DO NOT short across terminals PA and PC or across the DC bus capacitors.
• Install and close all covers before applying power or starting and stopping the drive.
• Before servicing the variable speed drive
- Disconnect all power
- Place a "DO NOT TURN ON" label on the variable speed drive disconnect
- Lock the disconnect in the open position
• Disconnect all power including external control power that may be present before
servicing the drive. Wait for the charging LED to go off. Then follow the DC bus voltage
measurement procedure on page 18 to verify that the DC voltage is less than 45 VDC.
The drive LEDs are not accurate indicators of the absence of DC bus voltage.
Electric shock will result in death or serious injury.
CAUTION
IMPROPER DRIVE OPERATION
• If the drive is not switched on for a long period, the performance of its electrolytic
capacitors will be reduced.
• If it is stopped for a prolonged period, turn the drive on every two years for at least
5 hours to restore the performance of the capacitors, then check its operation. It is
recommended that the drive is not connected directly to the line voltage. The voltage
should be increased gradually using an adjustable AC source.
Failure to follow these instructions can result in equipment damage.
Steps for setting up the drive
Steps 1 to 4 must
be performed with
the power off
DAMAGED PACKAGING
If the packaging appears damaged, it can be dangerous to open and handle it.
Take precautions against all risks when performing this operation.
Failure to follow these instructions can result in death or serious injury.
DAMAGED EQUIPMENT
Do not operate or install any drive that appears damaged.
Failure to follow these instructions can result in death or serious injury.
60°
max.
ATV71
DC choke
Preliminary recommendations
Precautions
If the safety of personnel requires the prohibition of unwanted or unexpected starts, electronic locking is performed by the
Altivar 71's “Power Removal” function.
This function requires the use of connection diagrams conforming to category 3 of standard EN 954-1 and safety integrity level 2
according to IEC/EN 61508.
The Power Removal function takes priority over any run command.
Read and understand the instructions in the "programming manual".
INCOMPATIBLE LINE VOLTAGE
Before switching on and configuring the drive, ensure that the line voltage is compatible with the supply voltage range
shown on the drive nameplate. The drive may be damaged if the line voltage is not compatible.
Failure to follow these instructions can result in equipment damage.
UNINTENDED EQUIPMENT OPERATION
• Before switching on and configuring the Altivar 71, check that the PWR (POWER REMOVAL) input is deactivated (at
state 0) in order to prevent unexpected starts. Do not forget to reactivate the Power Removal input to start the motor.
• Before switching on or on exiting the configuration menus, check that the inputs assigned to the run command are
deactivated (at state 0) since they can cause the motor to start immediately.
Failure to follow these instructions will result in death or serious injury.
Drive ratings
3-phase supply voltage: 200…240 V 50/60 Hz
3-phase motor 200...240 V
3-phase supply voltage: 380…480 V 50/60 Hz
3-phase motor 380...480 V
(1)These power ratings and currents are given for an ambient temperature of 50°C (122°F) and at the factory-set switching frequency of
2.5 kHz, used in continuous operation.
Above 2.5 kHz, the drive will reduce the switching frequency automatically in the event of excessive temperature rise. For continuous
operation above the factory setting, derating must be applied to the drive nominal current in accordance with the curves on pages 14
and 15.
(2)Current on a line supply with the "Max. prospective line Isc" indicated.
(3)The drives are supplied as standard with a DC choke which must be used for connecting the drive on a 3-phase line supply.
For connections on the DC bus, the drive can be controlled without a choke. Add the letter D at the end of the reference.
Example: ATV 71HD90N4 becomes ATV 71HD90N4D.
(4) If the drive is installed on a line supply with a prospective short circuit current that is higher than the value given in this column, use line
reactors (please refer to the catalog).
Motor Line supply (input) Drive (output) Altivar 71
Power
indicated on
plate (1)
Max. line current (2)(4) Max.
prospective
line Isc
Apparent
power
Nominal
current In
(1)
Max. transient
current
for (1)
Reference (3)
at 200 V at 240 V 60 s 2 s
kW HP A A kA kVA A A A
55 75 202 171 35 70.5 221 332 365 ATV71HD55M3X
75 100 274 231 35 95.4 285 428 470 ATV71HD75M3X
Motor Line supply (input) Drive (output) Altivar 71
Power
indicated on
plate (1)
Max. line current (2) Max.
prospective
line Isc
Apparent
power
Max.
available
nominal
current In
(1)
Max. transient current
for (1)
Reference (3)
at 380 V at 480 V 60 s 2 s
kW HP A A kA kVA A A A
90 125 166 134 35 109.3 179 295 268 ATV71HD90N4
110 150 202 163 35 133 215 354 322 ATV71HC11N4
132 200 239 192 35 157 259 427 388 ATV71HC13N4
160 250 289 233 50 190.2 314 518 471 ATV71HC16N4
200 300 357 286 50 235 387 638 580 ATV71HC20N4
220 350 396 320 50 260.6 427 704 640 ATV71HC25N4
250 400 444 357 50 292.2 481 793 721
280 450 494 396 50 325.1 550 907 825 ATV71HC28N4
315 500 555 444 50 365.3 616 1016 924 ATV71HC31N4
355 - 637 512 50 419.3 671 1107 1006 ATV71HC40N4
400 600 709 568 50 466.6 759 1252 1138
500 800 876 699 50 576.6 941 1552 1411 ATV71HC50N4
9
Dimensions and weights
(1)For the addition of I/O extension cards, communication cards, or the "Controller Inside" programmable card.
ATV71H a
D55M3X, D90N4 310
With 0 or 1 option card (1) With 2 option cards (1) ATV71H C31N4 to C40N4 ATV71H C50N4
Installing the DC choke
This should be performed after mounting the drive and before wiring it.
During installation, ensure that no liquid, dust or conductive objects fall into the drive.
Example of installing DC chokes on an ATV71HC16N4
- Mount the DC choke chassis on the wall, on top of the drive. Ensure that the chassis is tightly secured to the drive to maintain the
IP54 seal of the ventilation duct.
- Connect the grounding strip between the DC choke chassis and the drive.
- Then install the DC choke on the chassis using the nuts provided.
- Connect the choke between the PO and PA/+ terminals on the drive (see the next page).
- Then mount the cover on the chassis and secure it with the nuts provided.
- Then mount panels and using the screws provided.
Once the choke has been installed, the degree of protection of the top the drive is IP31.
Note: The number of DC chokes supplied with the drive varies according to the drive rating.
Connecting the DC choke
ATV71HD55M3X ... D75M3X, ATV71HD90N4 ... C13N4
ATV71HD55M3X to D75M3X and ATV71HD90N4 to C13N4 drives are supplied with one choke to be connected to the drive as shown
below.
ATV71HC16N4 ... C28N4
ATV71HC16N4 to C28N4 drives are supplied with two chokes to be connected to the drive as shown below.
PO PA/+
PO PA/+
Mounting and temperature conditions
Mounting a single drive
Install the drive vertically at ± 10°.
Do not place it close to heating elements.
Leave sufficient free space to ensure that the air required for cooling purposes can
circulate from the bottom to the top of the unit.
Free space in front of the drive: 10 mm (0.39 in.) minimum
Mounting several drives side by side
These drives can be mounted side by side, observing the following mounting recommendations:
ATV71H h
mm in.
D55M3X, D75M3X, D90N4, C11N4 100 3.94
C13N4, C16N4 250 9.84
C20N4 ... C28N4 300 11.81
C31N4 ... C40N4 450 17.72
C50N4 550 21.65
u h u h
u 400 mm
u 15.75 in.
u 400 mm
u 15.75 in.
u 1000 mm
u 39.4 in.
Access barrier
required
14
Mounting and temperature conditions
Derating curves
Derating curves for the drive current In as a function of the temperature and switching frequency.
For intermediate temperatures (e.g. 55°C (131°F)), interpolate between 2 curves.
ATV71HD55M3X, HD75M3X ATV71HD90N4
ATV71HC11N4 ATV71HC13N4
ATV71HC16N4 ATV71HC20N4
50°C (122°F)
60°C (140°F)
Switching frequency
50°C (122°F)
60°C (140°F)
Switching frequency
40°C (104°F)
50°C (122°F)
60°C (140°F)
Switching frequency
40°C (104°F)
Mounting and temperature conditions
For intermediate temperatures (e.g. 55°C (131°F)), interpolate between 2 curves.
ATV71HC25N4 ATV71HC28N4
ATV71HC31N4 ATV71HC40N4
ATV71HC50N4
Switching frequency
50°C (122°F)
60°C (140°F)
40°C (104°F)
ATV71HC25N4 used with a 220 kW (350 HP) motor
ATV71HC25N4 used with a 250 kW (400 HP) motor
50°C (122°F)
60°C (140°F)
Switching frequency
40°C (104°F)
Mounting in a wall-mounted or floor-standing enclosure
Installing the heatsink inside the enclosure
The power dissipated by the drive power components is given in the table below.
Power dissipated
These levels of power dissipation are given for operation at nominal load and for a switching
frequency of 2.5 Hz.
The drive has a fan for cooling the power components. The air is circulated from the bottom to
the top of the unit via a duct (the duct is shown shaded gray on the diagram opposite). This duct
is isolated from the control section by IP54 protection. The DC choke extends this duct while
maintaining IP54 protection.
The drive dissipates a great deal of power which must be evacuated to the outside of the
enclosure.
Air inlets and outlets must be provided to ensure that the flow of air in the enclosure is at least
equal to the value given in the table below for each drive.
Several methods of evacuation are possible. The following is a proposed method for IP23 and
IP54 mounting.
IP23 mounting (standard operating conditions):
Figure 1
Install the drive on an enclosure baseplate.
Install the DC choke in accordance with the mounting recommendations.
The simplest mounting is to extend the IP54 duct between the upper outlet of the DC choke
and the top of the enclosure . Fixing points are provided for this purpose on the top of the
DC choke.
The hot air is thus evacuated to the outside and does not contribute towards increasing the
internal temperature of the enclosure.
It is advisable to add a plate approximately 150 mm from the top of the enclosure over the
air outlet opening to prevent foreign bodies falling into the drive cooling duct.
The air inlet can be via a grille on the bottom front panel of the enclosure door, in accordance
with the required flow rates given in the above table.
Figure 2
It is advisable to use a kit for IP31/NEMA type 1 conformity (to be ordered as an option) for
attaching the power cables. The design of the IP31 kit is based on the same principle as the
DC choke, and has an IP54 duct to help guide the incoming air.
Note:
- If the air in the power circuit is totally evacuated to the outside, very little power is dissipated
inside the enclosure. In this case, use the dissipated power table for dust and damp proof
flange mounting (see the next page).
- Connect all the additional metal parts to ground.
ATV71H Power dissipated ATV71H Power dissipated
W W
D55M3X 1715 C20N4 4930
D75M3X 2204 C25N4 5873
D90N4 2403 C28N4 6829
C11N4 2593 C31N4 7454
C13N4 2726 C40N4 9291
C16N4 3812 C50N4 11345
ATV71H Flow rate
m3/hour ft3/min
D55M3X, D90N4 402 236
D75M3X, C11N4 774 455
C13N4 745 438
C16N4 860 506
C20N4, C25N4, C28N4 1260 742
C31N4, C40N4 2100 1236
C50N4 2400 1412
2
1
Cooling duct for power
components.
IP54 insulation protection
2
1
Kit for IP31 or NEMA
type 1 conformity
ATV71
ATV71
Figure 2
Figure 1
1
2
17
Mounting in a wall-mounted or floor-standing enclosure
Mounting the heatsink inside the enclosure (continued)
IP54 mounting (standard operating conditions):
The drive must be mounted in an IP54 enclosure in certain environmental conditions: dust,
corrosive gases, high humidity with risk of condensation and dripping water, splashing liquid,
etc.
The simplest way of obtaining an enclosure with IP54 protection is to follow the mounting
recommendations for IP23 protection with the following 5 additional points:
1 Do not make an air inlet hole in the enclosure door. The air will enter through the bottom of
the enclosure via a plinth added for the purpose.
2 Add the IP31 or NEMA type 1 conformity kit in accordance with the mounting instructions.
3 Add an enclosure baseplate designed to provide IP54 protection around the power cables.
4 Add an air evacuation duct between the baseplate and the duct of the IP31 or NEMA type 1
conformity kit. The IP31 or NEMA type 1 conformity kit enables an extension duct to be
mounted. Drill a hole in the base of the enclosure to allow air to enter. Place seals around the
duct that has been added to maintain IP54 protection.
5 Add a 200 mm plinth at the bottom of the enclosure with grilles to allow air to enter.
Note: Connect all the additional metal parts to ground.
Dust and damp proof flange mounting (heatsink outside
the enclosure)
This mounting is used to reduce the power dissipated in the enclosure by locating the power
section outside the enclosure.
This requires the use of the dust and damp proof flange mounting kit VW3A9509...517
(please refer to the catalog).
The degree of protection for the drive mounted in this way becomes IP54.
To fit the kit to the drive, please refer to the manual supplied with the kit.
Power dissipated inside the enclosure for dust and damp proof
flange mounting
These levels of power dissipation are given for operation at nominal load and for the factoryset
switching frequency.
(1)Add 7 W to this value for each option card added
ATV71H Power dissipated (1) ATV71H Power dissipated (1)
W W
D55M3X 154 C20N4 493
D75M3X 154 C25N4 586
D90N4 237 C28N4 658
C11N4 261 C31N4 772
C13N4 296 C40N4 935
C16N4 350 C50N4 1116
2
1
5
4
ATV71
3
2
18
Installing the kit for IP31/NEMA type 1 conformity
On ATV71H D55M3X to D75M3X and D90N4 to C50N4 drives, the cable shielding can be attached and connected to ground using one of
the following two kits:
• Kit for IP31 conformity (VW3 A9 109 ... 116)
• Kit for NEMA Type 1 conformity (VW3 A9 209 ... 216)
This kit is not supplied with the drive. It must be ordered separately (please refer to the catalog). It is mounted under the drive as shown
below.
- Mount the chassis on the wall or in the bottom of the enclosure under the drive. Ensure that the chassis is tightly secured to the
drive to maintain the IP54 seal of the ventilation duct.
- Mount the EMC plate on the kit chassis using the screws provided.
- Mount the bridge to ensure equipotentiality of the grounds between the drive and the EMC plate.
- Then mount the IP31 or NEMA type 1 cover on the EMC plate using the screws provided.
Position of the charging LED
Before working on the drive, turn it off, wait until the red capacitor charging LED has gone out, then measure the DC bus voltage.
Position of the capacitor charging LED
Procedure for measuring the DC bus voltage
The DC bus voltage can exceed 1000 V c. Use a properly rated voltage sensing device when performing this procedure. To measure the
DC bus voltage:
1 Disconnect the drive power supply.
2 Wait for the capacitor charging LED to go off.
3 Measure the voltage of the DC bus between the PA/+ and PC/- terminals to check whether the voltage is less than 45 V c.
Refer to page 25 for the layout of the power terminals.
4 If the DC bus capacitors have not discharged completely, contact your local Schneider Electric agent (do not repair or operate the drive).
Red LED indicating that the DC bus is switched on
DANGER
HAZARDOUS VOLTAGE
Read and understand the precautions on page 4 before performing this procedure.
Failure to follow these instructions will result in death or serious injury.
21
Installing option cards
These should ideally be installed once the drive is mounted and before wiring it.
Check that the red capacitor charging LED has gone out. Measure the DC bus voltage in accordance with the procedure indicated on
page 20.
The option cards are installed under the drive control front panel. Remove the graphic display terminal then take off the control front panel
as indicated below.
Removing the control front panel
ATV71H D55M3X to D75M3X and ATV71H D90N4 to C50N4 drives are supplied with an option card support already installed.
If adding an I/O or communication option card or a "Controller Inside" programmable card, remove the support using the same
mounting/removal procedure as for an option card. This card support serves no purpose when at least one option card is used.
Installing an encoder interface card
There is a special slot on the drive for adding an encoder interface card.
1 2 3
• Using a screwdriver, press down on
the catch and pull to release the lefthand
part of the control front panel
• Do the same on the
right-hand side
• Pivot the control front panel
and remove it
4
If an I/O or communication option card or a "Controller Inside"
programmable card has already been installed, remove it so you can
access the slot for the encoder feedback card.
22
Installing option cards
Installing an I/O extension card, a communication card or a "Controller Inside" programmable card
Install an encoder interface card (if used)
(see previous page)
Position the option card on the clasps
Then pivot it until it clicks into place
4
5
6
Replace the control front panel over the option card
(same procedure as for installing the option card, see and )
7
5 6
6
5
7
, and Remove the control front panel
(see previous page)
1 2 3
23
Wiring recommendations
Power
The drive must be connected to the protective ground. To comply with current regulations concerning high leakage currents (above 3.5 mA),
use at least a 10 mm? (AWG 6) protective conductor or 2 protective conductors with the same cross-section as the power section AC supply
conductors.
• Check whether the resistance to the protective ground is one ohm or less. Connect a number of
variable speed drives to the protective ground, as shown in the diagram (see left). Do not lay
protective grounding cables in a loop or in series.
When upstream protection by means of a "residual current device" is required by the installation standards, a type A device should be used
for single phase drives and type B for 3-phase drives. Choose a suitable model incorporating:
• HF current filtering
• A time delay which prevents tripping caused by the load from stray capacitance on power-up. The time delay is not possible for 30 mA
devices. In this case, choose devices with immunity against accidental tripping, for example "residual current devices" with reinforced
immunity from the s.i range (Merlin Gerin brand).
If the installation includes several drives, provide one "residual current device" per drive.
WARNING
IMPROPER WIRING PRACTICES
• The ATV71 drive will be damaged if input line voltage is applied to the output terminals (U/T1,V/T2,W/T3).
• Check the power connections before energizing the ATV71 drive.
• If replacing another drive, verify that all wiring connections to the ATV71 drive comply with all wiring instructions in this
manual.
Failure to follow these instructions can result in death or serious injury.
WARNING
INADEQUATE OVERCURRENT PROTECTION
• Overcurrent protective devices must be properly coordinated.
• The Canadian Electricity Code and the National Electrical Code require branch circuit protection. Use the fuses
recommended on the drive nameplate to achieve published short-circuit current ratings.
• Do not connect the drive to a power feeder whose short-circuit capacity exceeds the drive short-circuit current rating
listed on the drive nameplate.
Failure to follow these instructions can result in death or serious injury.
DANGER
HAZARDOUS VOLTAGE
Ground equipment using the provided ground connecting point as shown in the figure below. The drive panel must be
properly grounded before power is applied.
Failure to follow these instructions will result in death or serious injury.
variable
speed drive
variable
speed drive
variable
speed drive
24
Wiring recommendations
Keep the power cables separate from circuits in the installation with low-level signals (detectors, PLCs, measuring apparatus, video,
telephone).
The motor cables must be at least 0.5 m (20 in.) long.
Do not immerse the motor cables in water.
Do not use lightning arresters or power factor correction capacitors on the variable speed drive output.
Control
Keep the control circuits away from the power circuits. For control and speed reference circuits, we recommend using shielded twisted
cables with a pitch of between 25 and 50 mm (0.98 and 1.97 in.) and connecting the shielding to ground at each end.
If using conduit, do not lay the motor, power supply and control cables in the same conduit. Keep the metal conduit containing the power
supply cables at least 8 cm (3 in.) away from the metal conduit containing the control cables. Keep the non-metal conduits or cable ducts
containing the power supply cables at least 31 cm (12 in.) away from the metal conduits containing the control cables. If it is necessary for
control and power cables to cross each other, be sure they cross at right angles.
Length of motor cables
Choice of associated components:
Please refer to the catalog.
CAUTION
IMPROPER USE OF A BRAKING RESISTOR
• Only use the braking resistors recommended in our catalogs.
• Wire a thermal overload relay in the sequence or configure the braking resistor protection fault (please refer to the
programming manual) so that the drive power section AC supply is disconnected immediately in the event of a fault.
Failure to follow these instructions can result in equipment damage.
0 ... 50 m
(0 ... 164 ft)
50 ... 100 m
(164 ... 328 ft)
100 ... 150 m
(328 ... 492 ft)
150 ... 300 m
(492 ... 984 ft)
300 ... 600 m
(984 ... 1968 ft)
600 ... 1000 m
(1968 ... 3280 ft)
ATV71HpppM3X
ATV71HD90N4 to C50N4
Shielded
cable Motor choke Sinus filter
Unshielded
cable Motor choke Sinus filter
25
Power terminals
Access to the power terminals
To access the power terminals, unscrew the front panel and remove the protective cover
Characteristics and functions of the power terminals
(1)The ATV71H C40N4 and C50N4 have two input bridges. The power section AC supply is connected on terminals R/L1A - R/L1B, S/L2A
- S/L2B and T/L3A - T/L3B.
(2) From the ATV71HC20N4 upwards, there are no braking resistor connection terminals on the drive as the braking unit is optional (please
refer to the catalog). The braking resistor is then connected on the braking unit.
Terminal Function Altivar
3 x t Protective ground connection terminals All ratings
R/L1, S/L2, T/L3 (1) Power section AC supply All ratings
PO, PA/+ + polarity for connecting the DC choke All ratings
PC/- DC bus - polarity All ratings
PA/+ Output to braking resistor ATV71H D55M3X, D75M3X
PB Output to braking resistor ATV71H D90N4 to C16N4 (2)
U/T1, V/T2, W/T3 Output to the motor All ratings
DC bus power supply
• Power section AC supply
• Output to the motor
• Connections to ground
• Output to braking resistor (up
to ATV71HC16N4 rating only)
26
Power terminals
ATV71H D55M3X, D90N4
Wire size
View from below
View from above
Front view
31
Power terminals
ATV71H C31N4
Drive terminals L1/R, L2/S, L3/T U/T1, V/T2, W/T3 PC/-, PO, PA/+
ATV 71HC31N4 3 x (3 x 185 mm2) 3 x (3 x 150 mm2) 4 x 185 mm2
3 x 350 MCM 3 x 350 MCM 5 x 300 MCM
32
Power terminals
ATV71HC40N4
Wire size
Drive terminals L1/R, L2/S, L3/T U/T1, V/T2, W/T3 PC/-, PO, PA/+
ATV 71HC40N4 Motor P 350 kW
(550 HP)
2 x 2 x (3 x 150 mm2) 3 x (3 x 150 mm2) 4 x 185 mm2
2 x 2 x 300 MCM 5 x 300 MCM 6 x 300 MCM
Motor P 400 kW
(600 HP)
2 x 2 x (3 x 185 mm2) 3 x (3 x 185 mm2) 4 x 240 mm2
2 x 2 x 300 MCM 5 x 300 MCM 2 x 3 x 350 MCM
33
Power terminals
ATV71HC50N4
Wire size
Drive terminals L1/R, L2/S, L3/T U/T1, V/T2, W/T3 PC/-, PO, PA/+
ATV 71HC50N4 2 x 3 x (3 x 150 mm2) 4 x (3 x 185 mm2) 4 x 240 mm2
2 x 3 x 300 MCM 6 x 300 MCM 2 x 3 x 350 MCM
34
Control terminals
Access to the control terminals
To access the control terminals,
open the cover on the control front panel
Removing the terminal card
To make it easier to wire the drive control section,
the control terminal card can be removed.
• Undo the screw until the spring is fully extended
• Remove the card by sliding it downwards
Layout of the control terminals
Maximum wire size:
2.5 mm? - AWG 14
Max. tightening torque:
0.6 Nm - 5.3 lb.in
Note: The ATV71 is supplied with a link between the PWR and +24 terminals.
CAUTION
IMPROPERLY SECURED TERMINAL CARD
When replacing the control terminal card, it is essential to
fully tighten the captive screw.
Failure to follow these instructions can result in
equipment damage.
Logic input switch
LI6 input switch
RJ45 connector
Factory setting: Source
Factory setting: LI
35
Control terminals
Characteristics and functions of the control terminals
Terminal Function Electrical characteristics
R1A
R1B
R1C
Common point C/O contact (R1C) of
programmable relay R1
• Minimum switching capacity: 3 mA for 24 V c
• Maximum switching capacity on resistive load:
5 A for 250 V a or 30 V c
• Maximum switching current on inductive load (cos ? = 0.4 L/R = 7 ms):
2 A for 250 V a or 30 V c
• Reaction time: 7 ms ± 0.5 ms
• Service life: 100,000 operations at max. switching power
R2A
R2C
N/O contact of programmable relay R2
+10 +10 V c power supply for reference
potentiometer
1 to 10 k?
• +10 V c (10.5 V ± 0.5V)
• 10 mA max.
AI1+
AI1 -
Differential analog input AI1 • -10 to +10 V c (max. safe voltage 24 V)
• Reaction time: 2 ms ± 0.5 ms, 11-bit resolution + 1 sign bit
• Accuracy ± 0.6% for ?? = 60°C (140°F), linearity ± 0.15% of max. value
COM Analog I/O common 0V
AI2 Depending on software configuration:
Analog voltage input
or
Analog current input
• Analog input 0 to +10 V c (max. safe voltage 24 V),
impedance 30 k?
or
• Analog input X - Y mA, X and Y can be programmed from 0 to 20 mA
• Impedance 250 ?
• Reaction time: 2 ms ± 0.5 ms
• 11-bit resolution, accuracy ± 0.6% pour ?? = 60°C (140°F), linearity ± 0.15% of max.
value
COM Analog I/O common 0V
AO1 Depending on software configuration:
Analog voltage output
or
Analog current output
• Analog output 0 to +10 V c, load impedance greater than 50 k?
or
• Analog output X - Y mA, X and Y can be programmed from 0 to 20 mA
• Max. load impedance 500 ?
• 10-bit resolution, reaction time: 2 ms ± 0.5 ms
• Accuracy ± 1% for ?? = 60°C (140°F), linearity ± 0.2% of max. value
P24 Input for external +24 Vc control
section power supply
• +24 V c (min. 19 V, max. 30 V)
• Power 30 Watts
0V Logic input common and 0V of P24
external power supply
0V
LI1
LI2
LI3
LI4
LI5
Programmable logic inputs • +24 V c (max. 30 V)
• Impedance 3.5 k?
• Reaction time: 2 ms ± 0.5 ms
LI6 Depending on the position of the SW2
switch:
- Programmable logic input
or
- Input for PTC probes
SW2 switch on LI (factory setting)
• Same characteristics as logic inputs LI1 to LI5
or
SW2 switch on PTC
• Trip threshold 3 k?, reset threshold 1.8 k?
• Short-circuit detection threshold < 50 ?
+24 Logic input power supply SW1 switch in Source or Int Sink position
• +24 V c power supply (min. 21 V, max. 27 V), protected against short-circuits and
overloads
• Max. current available for customers 200 mA
SW1 switch in Ext Sink position
• Input for external +24 V c power supply for the logic inputs
PWR Power Removal safety function input
When PWR is not connected to the
24V, the motor cannot be started
(compliance with functional safety
standard EN 954-1 and IEC/
EN 61508)
• 24 V c power supply (max. 30 V)
• Impedance 1.5 k?
• State 0 if < 2 V, state 1 if > 17 V
• Reaction time: 10 ms
SW1 switch State 0 State 1
Source (factory setting) < 5 V c > 11 V c
Int Sink or Ext Sink > 16 V c < 10 V c
36
Option terminals
Logic I/O option card terminals (VW3 A3 201)
Maximum wire size:
1.5 mm? - AWG 16
Max. tightening torque:
0.25 Nm - 2.21 lb.in
Characteristics and functions of the terminals
Terminal Function Electrical characteristics
R3A
R3B
R3C
Common point C/O contact R3C of
programmable relay R3
• Minimum switching capacity: 3 mA for 24 V c
• Maximum switching capacity on resistive load:
5 A for 250 V a or 30 V c
• Maximum switching capacity on inductive load (cos ? = 0.4 L/R = 7 ms):
2 A for 250 V a or 30 V c
• Reaction time: 7 ms ± 0.5 ms
• Service life: 100,000 operations
-10 -10 V c power supply for reference
potentiometer 1 to 10 k?
• - 10 V c (-10.5 V ± 0.5V)
• 10 mA max.
+24 Logic input power supply SW3 switch in Source or Int Sink position
• +24 V c power supply (min. 21 V, max. 27 V), protected against short-circuits and
overloads
• Max. current available for customers 200 mA (This current corresponds to the total
consumption on the control card +24 and the option cards +24)
SW3 switch in Ext Sink position
• Input for external +24 V c power supply for the logic inputs
LI7
LI8
LI9
LI10
Programmable logic inputs • +24 V c power supply (max. 30 V)
• Impedance 3.5 k?
• Reaction time 2 ms ± 0.5 ms
0 V 0 V 0 V
TH1+ PTC probe input • Trip threshold 3 k?, reset threshold 1.8 k?
• Short-ci TH1- rcuit detection threshold < 50 ?
LO1
LO2
Open collector programmable logic
outputs
• +24 V c (max. 30 V)
• Max. current 200 mA for internal power supply and 200 mA for external power supply
• Reaction time: 2 ms ± 0.5 ms
CLO Logic output common
0V 0 V 0 V
R3A
TH1+
SW3
R3C
R3B
0V
-10
+24
LI7
LI8
LI9
LI10
TH1-
L01
L02
CLO
0V
Ext
Source
Sink
Int
Logic input switch SW3
Factory setting: Source
Switch SW3 State 0 State 1
Source (factory setting) < 5 V c > 11 V c
Int Sink or Ext Sink > 16 V c < 10 V c
37
Option terminals
Extended I/O option card terminals (VW3 A3 202)
Maximum wire size:
1.5 mm? - AWG 16
Max. tightening torque:
0.25 Nm - 2.21 lb.in
Characteristics and functions of the terminals
Terminal Function Electrical characteristics
R4A
R4B
R4C
Common point C/O contact R4C of
programmable relay R4
• Minimum switching capacity: 3 mA for 24 V c
• Maximum switching capacity on resistive load:
5 A for 250 V a or 30 V c
• Maximum switching capacity on inductive load (cos ? = 0.4 L/R = 7 ms):
1.5 A for 250 V a or 30 V c
• Reaction time 10 ms ± 1 ms
• Service life: 100,000 operations
-10 -10 V c power supply for reference
potentiometer 1 to 10 k?
• - 10 V c (-10.5 V ± 0.5V)
• 10 mA max.
AI3 + + polarity of the current differential
analog input AI3
• Analog input X - Y mA, X and Y can be programmed from 0 to 20 mA,
impedance 250 ?
• Reaction time: 5 ms ± 1 ms
• 11-bit resolution + 1 sign bit, accuracy ± 0.6% for ?? = 60°C (140°F)
• Linearity ± 0.15% of max. value
AI3 - - polarity of the current differential
analog input AI3
AI4 Depending on software configuration:
Analog current input
or
Analog voltage input
• Analog input 0 to +10 V c (max. safe voltage 24 V),
impedance 30 k?
or
• Analog input X - Y mA, X and Y can be programmed from 0 to 20 mA,
impedance 250 ?
• Reaction time: 5 ms ± 1 ms
• 11-bit resolution, accuracy ± 0.6% pour ?? = 60°C (140°F), linearity ± 0.15% of max.
value
COM Analog I/O common 0 V
AO2
AO3
Depending on software configuration:
Analog voltage outputs
or
Analog current outputs
• 0 - 10 V c or -10/+10 V c bipolar analog output depending on software
configuration, load impedance greater than 50 k?
or
• Analog current output X-Y mA, X and Y can be programmed from 0 to 20 mA, max.
load impedance 500 ?
• 10-bit resolution
• Reaction time 5 ms ± 1 ms, accuracy ± 1% for ?? = 60°C (140°F), linearity ± 0.2%
R4A
0V
SW4
TH2+
R4B
AO3
R4C
-10
AI3+
AI3-
AI4
COM
AO2
+24
LI11
LI12
LI13
LI14
CLO
0V
LO4
LO3
RP
TH2-
Ext
Source
Sink
Int
Logic input switch SW4
Factory setting: Source
38
Option terminals
Terminal Function Electrical characteristics
+24 Logic input power supply SW4 switch in Source or Int Sink position
• +24 V c output (min. 21 V, max. 27 V), protected against short-circuits and overloads
• Max. current available for customers 200 mA (This current corresponds to the total
consumption on the control card +24 and the option cards +24)
SW4 switch in Ext Sink position
• Input for external +24 V c power supply for the logic inputs
LI11
LI12
LI13
LI14
Programmable logic inputs • +24 V c (max. 30 V)
• Impedance 3.5 k?
• Reaction time: 5 ms ± 1 ms
0V Logic input common 0 V
TH2 +
TH2 -
PTC probe input • Trip threshold 3 k?, reset threshold 1.8 k?
• Short-circuit detection threshold < 50 ?
RP Frequency input • Frequency range: 0…30 kHz
• Cyclic ratio: 50% ± 10%
• Maximum sampling time: 5 ms ± 1 ms
• Maximum input voltage 30 V, 15 mA
• Add a resistor if the input voltage is greater than 5 V (510 ? for 12 V,
910 ? for 15 V, 1.3 k? for 24 V)
• State 0 if < 1.2 V, state 1 if > 3.5 V
LO3
LO4
Open collector programmable logic
outputs
• +24 V c (max. 30 V)
• Max. current 20 mA for internal power supply and 200 mA for external power supply
• Reaction time 5 ms ± 1 ms
CLO Logic output common
0V 0 V 0 V
SW4 switch State 0 State 1
Source (factory setting) < 5 V c > 11 V c
Int Sink or Ext Sink > 16 V c < 10 V c
39
Option terminals
Encoder interface card terminals
Maximum wire size:
1.5 mm? - AWG 16
Max. tightening torque:
0.25 Nm - 2.21 lb.in
Characteristics and functions of the terminals
Encoder interface cards with RS422-compatible differential outputs
Encoder interface cards with open collector outputs
Encoder interface cards with push-pull outputs
Terminal Function Electrical characteristics
VW3 A3 401 VW3 A3 402
+Vs Encoder power
supply
• 5 V c (max. 5.5 V) protected against short-circuits
and overloads
• Max. current 200 mA
• 15 V c (max. 16 V) protected against short-circuits
and overloads
• Max. current 175 mA
0Vs
A, /A
B, /B
Incremental
logic inputs
• Max. resolution: 10000 points/rev.
• Max. frequency: 300 kHz
Terminal Function Electrical characteristics
VW3 A3 403 VW3 A3 404
+Vs Encoder power
supply
• 12 V c (max. 13 V) protected against short-circuits
and overloads
• Max. current 175 mA
• 15 V c (max. 16 V) protected against short-circuits
and overloads
• Max. current 175 mA
0Vs
A, /A
B, /B
Incremental
logic inputs
• Max. resolution: 10000 points/rev.
• Max. frequency: 300 kHz
Terminal Function Electrical characteristics
VW3 A3 405 VW3 A3 406 VW3 A3 407
+Vs Encoder power
supply
• 12 V c (max. 13 V) protected
against short-circuits and
overloads
• Max. current 175 mA
• 15 V c (max. 16 V) protected
against short-circuits and
overloads
• Max. current 175 mA
• 24 V c (min. 20 V, max. 30 V)
protected against short-circuits
and overloads
• Max. current 100 mA
0Vs
State 0 If <1.5 V
State 1 If > 7.7 V and < 13 V If > 7.7 V and < 16 V If > 11.5 V and < 25 V
A, /A
B, /B
Incremental
logic inputs
• Max. resolution: 10000 points/rev.
• Max. frequency: 300 kHz
VW3 A3 401...407
A
A
B
B
0Vs
+Vs
40
Option terminals
Selecting the encoder
The 7 encoder interface cards available as options with the ATV71 enable three different encoder technologies to be used.
• Optical incremental encoder with differential outputs compatible with the RS422 standard
• Optical incremental encoder with open collector outputs
• Optical incremental encoder with push-pull outputs
The encoder must comply with the following two limits:
• Maximum encoder frequency 300 kHz
• Maximum resolution 10000 points/revolution
Choose the max. standard resolution within these limits to obtain optimum accuracy.
Wiring the encoder
Use a shielded cable containing 3 twisted pairs with a pitch of between 25 and 50 mm (0.98 in. and 1.97 in.). Connect the shielding to ground
at both ends.
The minimum cross-section of the conductors must comply with the table below to limit line voltage drop:
Max. length of
encoder cable
VW3 A3 401...402 VW3 A3 403...407
Max. consumption
current of encoder
Minimum cross-section of
conductors
Max. consumption
current of encoder
Minimum cross-section of
conductors
10 m
32.8 ft
100 mA 0.2 mm? AWG 24 100 mA 0.2 mm? AWG 24
200 mA 0.2 mm? AWG 24 200 mA 0.2 mm? AWG 24
50 m
164 ft
100 mA 0.5 mm? AWG 20 100 mA 0.5 mm? AWG 20
200 mA 0.75 mm? AWG 18 200 mA 0.75 mm? AWG 18
100 m
328 ft
100 mA 0.75 mm? AWG 18 100 mA 0.75 mm? AWG 18
200 mA 1.5 mm? AWG 15 200 mA 1.5 mm? AWG 16
200 m
656 ft
- - - 100 mA 0.5 mm? AWG 20
- - - 200 mA 1.5 mm? AWG 15
300 m
984 ft
- - - 100 mA 0.75 mm? AWG 18
- - - 200 mA 1.5 mm? AWG 15
41
Connection diagrams
Connection diagrams conforming to standards EN 954-1 category 1 and
IEC/EN 61508 capacity SIL1, stopping category 0 in accordance with standard
IEC/EN 60204-1
Diagram with line contactor
Diagram with switch disconnect
(1) Line reactor (if used)
(2) Fault relay contacts for remote signaling of drive status
(3) For the wiring of the power section AC supply for ATV71HC40N4 and ATV71HC50N4 drives please refer to page 44.
Note: Install interference suppressors on all inductive circuits near the drive or connected to the same circuit (relays, contactors, solenoid
valves, etc).
Choice of associated components:
Please refer to the catalog.
U / T1
V / T2
W / T3
R / L1
M
3 a
S / L2
T / L3
+24
PWR
A1
R1A
R1C
R1B
R2A
R2C
(2)
- KM1
- KM1
- S2 - S1 A1 A2
R1A R1C
- KM1
- Q2 - T1 - Q3
- Q2
A1
U1
W1
V1
(1)
(3) (3) (3)
U / T1
V / T2
W / T3
R / L1
U1
W1
V1
M
3 a
S / L2
T / L3
PWR
+24
A1
R1A
R1C
R1B
R2A
R2C
(1)
(2)
Q1
(3) (3) (3)
42
Connection diagrams
Connection diagrams conforming to standards EN 954-1 category 3 and
IEC/EN 61508 capacity SIL2, stopping category 0 in accordance with standard
IEC/EN 60204-1
This connection diagram is suitable for use with machines with a short freewheel stop time (with low inertia or high resistive torque).
When the emergency stop is activated, the drive power supply is turned off immediately and the motor stops in accordance with category 0
of standard IEC/EN 60204-1.
This diagram must be used for hoisting applications.
A contact on the Preventa XPS AC module must be inserted in the brake control circuit to engage it safely when the Power Removal safety
function is activated.
(1)Line reactor, if used.
(2)Fault relay contacts for remote signaling of drive status
(3) It is essential to connect the shielding on the cable connected to the Power Removal input to ground.
(4)For the wiring of the power section AC supply for ATV71HC40N4 and ATV71HC50N4 drives please refer to page 44.
- Standard EN 954-1 category 3 requires the use of a stop button with double contact (S1).
- S1 is used to activate the Power Removal safety function.
- S2 is used to initialize the Preventa module when switching on or after an emergency stop. ESC enables the use of other initialization
conditions for the module.
- One Preventa module can be used for the Power Removal safety function on several ATV71 drives.
- A logic input on the Preventa module can be used to indicate safely that the drive is operating in safe conditions.
Note:
For preventive maintenance, the Power Removal function must be activated at least once a year.
The drive power supply must be turned off and then on again before carrying out this preventive maintenance.
The drive logic output signals cannot be considered as safety-type signals.
Fit interference suppressors to all inductive circuits near the drive or coupled to the same circuit (relays, contactors, solenoid valves, etc).
Choice of associated components:
Please refer to the catalog.
U / T1
V / T2
W / T3
R / L1
U1
W1
V1
M
3 a
S / L2
T / L3
+24
PWR
A1
LI1
LI6
S2
A2 Y2 13 23 33
A2 PE 14 24 34
Y43
Y44
Y1
48 V, 115 V, 230 V K1 K2
K1
K2
T
ESC
XPS AC
S1
F1
LI2
N(-) L1(+)
(1)
(3)
R1A
R1C
R1B
(4) (4) (4) (2)
Logic
43
Connection diagrams
Connection diagram conforming to standards EN 954-1 category 3 and
IEC/EN 61508 capacity SIL2, stopping category 1 in accordance with standard
IEC/EN 60204-1
This connection diagram is suitable for use with machines with a long freewheel stop time (machines with high inertia or low resistive
torque).
This diagram must not be used for lifting applications.
When the emergency stop is activated, deceleration of the motor controlled by the drive is requested first. Then, after a time delay
corresponding to the deceleration time, the Power Removal safety function is activated.
Example:
- 2-wire control
- LI1 assigned to forward
- LI2 assigned to reverse
(1)Line reactor, if used.
(2)Fault relay contacts for remote signaling of drive status
(3) In this example, the logic inputs Lix are wired as "Source" but can be wired as "Int Sink" or "Ext Sink" (please refer to page 45).
(4) It is essential to connect the shielding on the cable connected to the Power Removal input to ground.
(5)For the wiring of the power section AC supply for ATV71HC40N4 and ATV71HC50N4 drives please refer to page 44.
- Standard EN 954-1 category 3 requires the use of an emergency stop with double contact (S1).
- S1 is used to activate the Power Removal safety function.
- S2 is used to initialize the Preventa module when switching on or after an emergency stop. ESC enables the use of other initialization
conditions for the module.
- One Preventa module can be used for the Power Removal safety function on several ATV71 drives. In this case the time delay must
be set to the longest stopping time.
- A logic input on the Preventa module can be used to indicate safely that the drive is operating in safe conditions.
Note: For preventive maintenance, the Power Removal function must be activated at least once a year.
The drive power supply must be turned off and then on again before carrying out this preventive maintenance.
The drive logic output signals cannot be considered as safety-type signals.
Install interference suppressors on all inductive circuits near the drive or coupled to the same circuit (relays, contactors, solenoid valves,
etc).
Choice of associated components:
Please refer to the catalog.
F1 S1
ESC
U / T1
V / T2
W / T3
R / L1
U1
W1
V1
M
3 a
S / L2
T / L3
+24
PWR
A1
LI1
LI6
LI2
A2 S21 S11
A2 PE Y1
13
T - +
115 V
230 V
2
K2
K1
K3
K4
K3 K1 K2
23
14 24 34 42 58 68
B1 S12 S22 33 41 57 67
S33
XPS AT
Y2 Y3
K4
K1 K2
K2
K1
1
Y4 Y5
K3
K4
S2
N(-) L1(-)
(1) (3)
(4)
R1A
R1C
R1B
(5) (5) (5) (2)
Logic
44
Connection diagrams
Power terminal connection diagram for ATV71HC40N4 and ATV71HC50N4 drives
(1) Line reactors (if used)
Braking resistor connection diagram
ATV71H D55M3X, D75M3X
ATV71H D90N4 to C16N4
Up to 16 kW power (ATV71HC16N4), braking resistors are connected directly to the terminals at the base of the drive (terminals PA/+ and
PB).
(1)Thermal overload relay
ATV71H C20N4 to C50N4
From 200 kW (ATV71HC20N4), the braking resistor is connected to the external braking unit between terminals PA+ and PB. Refer to the
braking unit user’s manual.
L1A
L2A
L3A
L1B
L2B
L3B
M1
3 a
U/T1
W/T3
V/T2
3 a
(1) (1)
PB
PA / +
TH
(1)
A1
ATV71
braking resistor
45
Connection diagrams
Control connection diagrams
Control card connection diagram
Logic input switch (SW1)
The logic input switch (SW1) is used to adapt the operation of the logic inputs to the technology of the programmable controller outputs.
• Set the switch to Source (factory setting) if using PLC outputs with PNP transistors.
• Set the switch to Int Sink or Ext Sink if using PLC outputs with NPN transistors.
• SW1 switch set to "Source" position • SW1 switch set to "Source" position and use of an external power
supply for the LIs
• SW1 switch set to "Int Sink" position • SW1 switch set to "Ext Sink" position
WARNING
Unintended Equipment Operation
• When the SW1 switch is set to "Int Sink" or "Ext Sink", the common must never be connected to ground or the protective
ground, as there is then a risk of accidental starting on the first insulation fault.
Failure to follow these instructions can result in death or serious injury.
LI1
LI5
+24
0V
A1 ATV71Hppppp
PWR
+10
AI1+
AI2
AI1-
COM
COM
AO1
LI3
LI2
LI6
LI4
Reference
potentiometer
0 ± 10 V
or
X-Y mA
A1 ATV71Hppppp
SW1
Ext
Source
Sink
Int
LI1
LI5
+24
0V
LI3
LI2
LI6
LI4
A1 ATV71Hppppp
SW1
Ext
Source
Sink
Int
LI1
LI5
+24
0V
LI3
LI2
LI6
LI4
+24 V
0 V
24 V c source
A1 ATV71Hppppp
SW1
Ext
Source
Sink
Int
LI1
LI5
+24
0V
LI3
LI2
LI6
LI4
A1 ATV71Hppppp
SW1
Ext
Source
Sink
Int
LI1
LI5
+24
0V
LI3
LI2
LI6
LI4
+24 V
0 V
24 V c source
46
Connection diagrams
Bipolar speed reference
Speed reference using axis control
SW2 switch
The LI6 logic input switch (SW2) makes it possible to use the LI6 input:
- either as a logic input by setting the switch to LI (factory setting)
- or for motor protection via PTC probes by setting the switch to PTC
Control power supply via an external source
The control card can be supplied via an external +24 V c source
- 10 V
+ 10 V
COM
AI1+
AI1-
A1
ATV71Hppppp
±10 V c source
+
COM
AI1+
AI1-
A1
ATV71Hppppp
0V
-
Axis control
±10 V
reference
0V
LI6
A1
ATV71Hppppp
PTC LI
SW2
Motor
A1
ATV71Hppppp
0V P24
+24 V
0 V
24 V c source
47
Connection diagrams
I/O extension card connection diagrams
Connection diagram for extended I/O option card (VW3A3202)
Connection diagram for logic I/O option card (VW3A3201)
+24
VW3A3202
0V
RP
CLO
LO4
LO3
LI11
0V
TH2+
TH2-
AO2
AO3
COM
AI4
AI3-
AI3+
R4A
R4C
R4B
A1
0 ± 10 V
or
X-Y mA
Motor
+24
VW3A3201
CLO
LO2
LO1
LI7
0V
TH1+
TH1-
R3A
R3C
R3B
A1
Motor
48
Connection diagrams
SW3/SW4 logic I/O switch
• Switch in "Source" position • Switch in "Source" position and use of an external +24 Vc source
• Switch in "Int Sink" position • Switch in "Ext Sink" position
WARNING
Unintended Equipment Operation
• When the SW3 or SW4 switches are set to "Int Sink" or "Ext Sink", the common must never be connected to ground or
the protective ground, as there is then a risk of accidental starting on the first insulation fault.
Failure to follow these instructions can result in death or serious injury.
A1
VW3 A3 20p
+24
CLO
LOp
LIp
0V
Ext
Source
Sink
Int
SW3 or SW4
+24V
0V
+24
CLO
LOp
LIp
0V
A1
VW3 A3 20p
Ext
Source
Sink
Int
24 V c source
SW3 or SW4
A1
+24
CLO
LOp
LIp
0V
VW3 A3 20p
Ext
Source
Sink
Int
SW3 or SW4
+24V
0V
+24
CLO
0V
LOp
LIp
A1
VW3 A3 20p
Ext
Source
Sink
Int
24 V c source
SW3 or SW4
49
Connection diagrams
Connection of several drives in parallel on the DC bus
Connection in parallel on the DC bus is recommended in applications for which full motor power must be guaranteed.
Connection on DC bus between drives with equivalent ratings
Each drive uses its own charging circuit
Drives , and must not be more than one size apart when they are connected in this way.
F1, F2, F3: fast-acting semi-conductor fuses for protection on the DC bus side.
Connection on DC bus between drives with different ratings
F1, F2, F3: fast-acting semi-conductor fuses for protection on the DC bus side.
F1 F2 F3
U / T1
V / T2
W / T3
U1
W1
V1
M1
3 a
ATV71Hppppp PO
PC/-
U / T1
V / T2
W / T3
U2
W2
V2
M2
3 a
ATV71Hppppp
PO
PC/-
U / T1
V / T2
W / T3
U3
W3
V3
M3
3 a
ATV71Hppppp PO
PC/-
1 2 3
R / L1
S / L2
T / L3
R / L1
S / L2
T / L3
R / L1
S / L2
T / L3
1 2 3
U/T1
V/T2
W/T3
R/L1
S/L2
T/L3
F2 F3
M1
ATV71Hppppp
F1
PO
PC/+
U/T1
V/T2
W/T3
ATV71Hppppp
PA/+
PC/-
U/T1
V/T2
W/T3
ATV71Hppppp
PA/+
PC/-
1 2 3
U1
W1
V1
3 a
M2
U2
W2
V2
3 a
M3
U3
W3
V3
3 a
50
Operation on an IT (Isolated or impedance grounded neutral) system
IT system: Isolated or impedance grounded neutral.
Use a permanent insulation monitor compatible with non-linear loads: a Merlin Gerin type XM200 or equivalent.
Altivar 71 drives feature built-in RFI filters. These filters can be isolated from ground for operation on an IT system as follows:
ATV71H D55M3X to D75M3X and ATV71H D90N4 to C11N4:
ATV71H C13N4 to C16N4:
CAUTION
When the filters are disconnected, the drive switching frequency must not exceed 4 kHz. Refer to the programming
manual for the corresponding parameter setting.
Failure to follow these instructions can result in equipment damage.
Normal
(filter connected)
IT system
(filter disconnected)
Normal
(filter connected)
IT system
(filter disconnected)
51
Operation on an IT (Isolated or impedance grounded neutral) system
ATV71H C20N4 to C50N4:
CAUTION
When the filters are disconnected, the drive switching frequency must not exceed 4 kHz. Refer to the programming
manual for the corresponding parameter setting.
Failure to follow these instructions can result in equipment damage.
Normal
(filter connected)
IT system
(filter disconnected)
52
Electromagnetic compatibility, wiring
Electromagnetic compatibility
Principle
• Grounds between drive, motor and cable shielding must have "high frequency" equipotentiality.
• Use of shielded cables with shielding connected to ground at both ends for the motor cables, braking resistor (if used) and control-signal
wiring. Conduits or metal ducting can be used for part of the shielding length provided that there is no break in continuity.
• Ensure maximum separation between the power supply cable (line supply) and the motor cable.
Installation diagram
ATV71H D55M3X to D75M3X and ATV71H D90N4 to D50N4
1 Altivar 71
2 Sheet steel grounded plate
3 Metal clamps
4 Shielded cable for motor connection, with shielding connected to
ground at both ends. The shielding must be continuous and
intermediate terminals must be in EMC shielded metal boxes.
5 Shielded cable for connecting the braking resistor (if used).
The shielding must be continuous and intermediate terminals must
be in EMC shielded metal boxes.
6 Shielded cables for connecting the control-signal wiring. For
applications requiring a large number of conductors, use cables with
a small cross-section (0.5 mm2).
7 Shielded cables for connecting the "Power Removal" safety
function input. The shielding must be continuous and intermediate
terminals must be in EMC shielded metal boxes.
8 Shielded cables for connecting the encoder. The shielding must be
continuous and intermediate terminals must be in EMC shielded
metal boxes.
9 Non-shielded wires for relay contact output
10 Connection to the protective ground
11 Non-shielded power supply wires or cable
Note:
• If using an additional input filter, it should be installed under the drive and connected directly to the line supply via an unshielded cable.
Link 4 on the drive is then via the filter output cable.
• The HF equipotential ground connection between the drive, motor and cable shielding does not remove the need to connect the PE
protective conductors (green-yellow) to the appropriate terminals on each unit.

Table of Contents

Before you begin______________________________________________________________________________________________ 4
Steps for setting up the drive ____________________________________________________________________________________ 5
Preliminary recommendations ___________________________________________________________________________________ 6
Drive ratings _________________________________________________________________________________________________ 8
Dimensions and weights________________________________________________________________________________________ 9
Installing the DC choke________________________________________________________________________________________ 11
Connecting the DC choke______________________________________________________________________________________ 12
Mounting and temperature conditions ____________________________________________________________________________ 13
Mounting in a wall-mounted or floor-standing enclosure ______________________________________________________________ 16
Installing the kit for IP31/NEMA type 1 conformity ___________________________________________________________________ 18
Position of the charging LED ___________________________________________________________________________________ 20
Installing option cards_________________________________________________________________________________________ 21
Wiring recommendations ______________________________________________________________________________________ 23
Power terminals _____________________________________________________________________________________________ 25
Control terminals_____________________________________________________________________________________________ 34
Option terminals _____________________________________________________________________________________________ 36
Connection diagrams _________________________________________________________________________________________ 41
Operation on an IT (Isolated or impedance grounded neutral) system ___________________________________________________ 50
Electromagnetic compatibility, wiring _____________________________________________________________________________ 52
4
Before you begin

Variable speed drives for acncrns mtrs atv71e_installation_manual_en_v1.pdf

Download [3 KB]

Thank U
Reply
refresh list

Similar releases

Hyundai Synchronous Brushless A.C Generators / Instruction Manual [PDF]
KRAL Screw pumps K Series with magnetic coupling / Operating Instructions [2006, PDF]
NMF Crane DK II 250012/100026 (Operating Manual + Assembly instruction) [2002, PDF]
Volute Casing Centrifugal Pumps Retain Series NI - ALLWEILER / Operating and Maintenance…
Marine Cargo Crane GPS 250-0818 - Norlift [2007, PDF]
LMG Marine Crane KL250/200/185/60t (Adjustment + Diagram) - TTS [1997, PDF]
Digital Temperature Micro-controller X Model: PXZ - Fuji Electric/ Instruction and Operation…
Hydraulic Crane PTM (Operators Manual) - Palfinger Marine [2006, PDF]
Desmi self-priming centrifugal pump Modular S / Operation and maintenance instruction [2003, PDF]
Waste oil incinerator unit type : MAXI 50SL-1 - Hyundai / Instruction book for installation,…
LOAD MORE
  • Reply

The time now is: Today 21:57

All times are GMT + 3 Hours